Home Renewables NREL Finds Greater Cycling from Renewable Penetration Does Not Significantly Increase Emissions
Much attention has been devoted recently to the increased cycling that is necessary in fossil plants as more renewable capacity is added to the grid, but data on the precise impacts has been slight. Now, a new study from the National Renewable Energy Laboratory (NREL) aims to correct that. The key findings: While cycling would increase with greater wind and solar penetration, and with it cycling costs, these would be more than offset by enormous fuel cost savings. In addition, the increased cycling would not increase emissions enough to offset savings from greater use of renewables.
The report is the second phase of the Western Wind and Solar Integration Study (WWSIS). WWSIS is supported by the Energy Department’s Office of Energy Efficiency and Renewable Energy, as well as its Office of Electricity Delivery and Energy Reliability. The study was undertaken by NREL, GE, Intertek-APTECH, and REPPAE. The first phase of WWSIS, released in May 2010, examined the viability, benefits, and challenges of integrating high concentrations of wind and solar power into the Western Interconnection grid. WWSIS-1 found it to be technically feasible if certain operational changes could be made, but also raised questions about the impact of cycling on wear-and-tear costs and emissions.
To calculate cycling costs and emissions impacts for WWSIS-2, NREL designed five scenarios modeling wind and solar penetration in the U.S. portion of the Western Interconnection in 2020. The scenarios included a 0% renewable baseline, the 2020 Portfolio Case (9.4% wind and 3.6% solar) created by the Western Electric Coordinating Council (WECC), and three different mixes of 33% penetration (high solar, high wind, and an equal mix). This was equivalent to 25% of the power in the Western Interconnection (including Canada and Mexico) coming from wind and solar energy on an annual basis.
The study assumed an average natural gas price of $4.60/MMBtu, significant cooperation between balancing authorities, and optimal usage of transmission capacity. NREL modeled operations of the Western Interconnection in five-minute intervals across the entire year to understand potential impacts each hour.
Greater Cycling Costs, But Big Fuel Savings
WWSIS-2 found that high wind and solar penetration would incur annual cycling costs that ranged from $35 million to $157 million a year, depending on the mix. For the average fossil plant, 33% wind and solar penetration would cause cycling costs to increase by $0.47MWh to $1.28/MWh. However, this level of penetration would displace annual fuel costs of approximately $7 billion. One interesting result was that overall cycling costs across the WECC and three 33% scenarios were largely similar. This suggests that most costs would come around the 15% penetration threshold and level off after that.
On emissions, the study found that increased cycling in these scenarios had only a minor impact compared to the gains that would be expected from displacing fossil generation. The differences were less than 5% either way. Carbon emissions reductions with more frequent cycling were <0.2% less than expected, while SO2 emissions reductions were 5% less than expected. However, emissions of nitrogen oxides were reduced 2% more than expected. Overall, 33% wind and solar energy penetration in the U.S. portion of the Western grid would avoid 29% to 34% CO2 emissions, 16% to 22% of NOx emissions, and 14% to 24% of SO2 emissions. (The study did not examine cycling impacts on mercury and air toxic control equipment.)
One reason for the largely negligible emissions impacts was that, not surprisingly, most of the cycling that occurred was in natural gas plants. The study found that, on average, 4 MWh of renewables would displace only 1 MWh of coal generation but 3 MWh of gas.
Increased Coal Ramping
Still, the biggest potential impact was the increase in ramping of coal units, but the precise impact varied significantly between the high solar and high wind scenarios (which assumed a 25%/8% mix of solar and wind or vice versa). Ramping increased more under high solar, but high wind displaced the most total coal generation.
During periods of low demand but good renewable generation in the spring, coal plants in the high solar scenario underwent significant daily ramping episodes. Coal ramping took place under the high wind scenario, but not as dramatically. The high wind scenario decreased the average coal runtime per start by a third, while the high solar scenario increased the number of ramps by an order of magnitude.
Because of this impact, the high solar scenario also had the highest cycling costs, ranging from $52 million to $157 million (the range reflects uncertainty in wear-and-tear). However, combustion turbine plants generally bore the large brunt of the increase in costs—again, because they bore the brunt of the cycling. But regardless of the plant type, cycling costs were dwarfed by the fuel savings (Figure 1).
NREL fig 1
1. Though increased ramping caused higher cycling costs in all scenarios, this was more than offset by savings in fuel costs. VOM = variable operations and maintenance; TEPPC = WECC Transmission Expansion Planning Policy Committee 2020 portfolio case. Courtesy: NREL
As comparison, the study also ran the models under two additional assumptions about future gas prices, $2.30/MMBtu and $9.20/MMBtu (in addition to the $4.60 base case). It found that changes in gas price had a larger impact on cycling costs than renewable penetration, because it had a dramatic effect on how gas-fired plants were used (i.e., baseload with cheap gas and peaking with expensive gas).
The authors conceded during a press call on the report that they did not have access to data on transmission or power purchase agreements that could be implicated by the potential changes. Thus, the study might have modeled more flexibility into the system than it would actually have.
The study also focused only on operational issues and did not consider other factors such as power market impacts, capital costs, or transmission costs. Future work at NREL may examine these issues.
—Thomas W. Overton, JD, gas technology editor.