Arcos de la Frontera Grupo III Combined-Cycle Plant, Cádiz, Spain
Pages: 12
Introducing the 9FB gas turbine
Unique configuration
Both Arcos I and II have a common driveline for the gas turbine and steam turbine, which drive a common generator from opposite ends. Such a 1x1 configuration is rare in the U.S. Each of the identical 400-MW (nominal) units (Table 1)—which produce in parallel—has a GE 9FA gas turbine rated at 248 MW (see box), an NEM heat-recovery steam generator (HRSG), and a GE D10 steam turbine rated at 136 MW. Two Alstom-supplied condensers sit under the steam turbine, whose drivelines are enclosed in a common building with the air inlet filter house mounted on the roof. The HRSGs are located outside the building. An auxiliary boiler supplies start-up steam. Arcos I and II use liquid fuel (with a maximum sulfur content of 0.2%) as backup.
Table 1. Combined-cycle performance at Arcos I through III. Source: Iberdrola
Arcos III, which is configured as a more-familiar 2 x1 800-MW power block, is the first commercial host of two GE 9FB turbines nominally rated at 259 MW apiece (Figure 5), two NEM multi-pressure HRSGs, and one 295-MW GE D11 steam turbine (Figure 6). In GE vernacular, this configuration is called a STAG (STeam And Gas) 209FB. Initial baseload operation was reached in late November 2005. The entire plant is designed for baseload operation (operation at full load for 8,500 hours a year). The output of Arcos III travels through a 400-kV substation at the plant to Red Eléctrica, Spain's national grid operator.
 6. Four-footers. The D11 steam turbine features 48-inch last-stage blades. Courtesy: Iberdrola
The steam turbine has a single high-pressure/intermediate-pressure (HP/IP) section and one dual-flow low-pressure (LP) section with control and shutoff valves for each of the three sections. The HP steam supply is at 1,800 psia and 1,050F, and the exhaust pressure is 1.73 inches Hg. The HP and IP stages have a bypass system, enabling steam to be desuperheated before entering the condenser. The bypass system activates whenever pressures fall to a predetermined setpoint and also during start-up and low-load operation to provide more operating flexibility. The D11 steam turbine is fitted with GE's new 48-inch last-stage blades.
The plant's distributed control system (DCS), located in the control room, handles overall plant control functions (via start-up, shutdown, and emergency operation signals), monitors field instrumentation, and controls auxiliary systems (Figure 7). Turbine controls for Arcos III, also in the control room, are provided by a triple-redundant GE Speedtronic Mark VI system. It directly controls and monitors the gas turbines, steam turbines, the three GE 330H generators (rated at 330/360 MVA), and other plant auxiliaries. The turbines are controlled by the Mark VI via a communications link with the DCS.
  7. Unified controls. Controls for the three power blocks are integrated in a single control room. Courtesy: Iberdrola
Iberdrola elected to construct a single building to house the control room and monitoring systems for the entire plant, as well as offices, shops, and storerooms. Three other buildings house the water treatment, compressed-air, fire protection, and other balance-of-plant systems.
Cooling water for the entire plant comes from the Guadalcacín II reservoir adjacent to the plant. Two mechanical-draft, counterflow cooling towers (Figure 8) with eight cells apiece cool circulating water. Exhaust gases are released to the atmosphere through twin 200-foot stacks.
8. Keeping cool. Arcos III uses cooling towers to cool condenser water. Shown are the cooling water pipes to the condenser. Courtesy: Iberdrola
Exceeding goals
Performance of the plant since commercial operation commenced has been exceptional, surpassing contract performance (Table 2) and emissions limits (Table 3) with room to spare. As of July 1, Unit 3 (Arcos III, gas turbine 1) had accumulated 1,968 fired hours and 92 starts. Unit 4 had 2,285 fired hours and 75 starts.
Table 2. Performance test results of Arcos III, corrected to ISO conditions. Source: Iberdrola
Table 3. 9FB emissions test results at Arcos III. Data are based on two 24-minute tests at part load and three 64-minute tests at baseload for each unit. All data shown are corrected to ppmv@15% O2. Source: Iberdrola
Pages: 12